Your numbers (amount of -134 and gauge pressures) do not make sense. Could be because of your variable displacement compressor. When converting to -134 you can only use about 80% of the fill you would use for R-12. Even at that, pressures will be higher than if you are using -12. Because the cooling capacity is based on the mass (amount) of refrigerant, your cooling capacity is reduced by about 20% when you use -134. Lock the compressor up at full tilt, remove some of the -134, check your pressures at 1,000 RPM. You should get a 20 degree temperature drop at the vents. Make sure you are in recirc mode and you don't have any large leaks into your doors.