Dry chemical extinguishers over time will clump and pack. You should invert and smack with a rubber mallet to loosen it up. You can tell by shaking them. If you try using one that has packed together no media comes out.
I recently shot one off that was a factory original Mercedes unit, in an 80 Mercedes 280SE. Had the MB logo and the passenger seat lower seat mount. Dry chemical unit. I figured there was no way it wad going to work, as it was pretty likely as old as the car... gauge still was reading good, and good it was. When fired it performed just as a brand new one would have.
Still rocking the Ducellier
Location: Burnsville MN-Moving to Kalispell MT. in June 20111
Posts: 886
My VIN: 2691
I ask the guy who services our apt. fire equipment if he had any halon exting. He did but he can't sell them anymore [EPA? environment thing?] He gave me a nice ten pounder for my car. Maybe it was just a MN. thing.
Location: Traverse City MI
Posts: 17
I had to get EPA Section 609 Certification to buy R-12 refrigerant because it's a CFC, might be a similar thing?
Location: Sacramento-ish
Posts: 4,408
My VIN: 02100
Club(s): (NCDMC) (DCUK)
It's somewhat more extreme than even that. Details for those who are truly interested can be found here: http://www.epa.gov/ozone/snap/fire/qa.html
Jon
1981 DMC-12 #02100. July 1981. 5-speed, black, grooved w/flap.
restoration log, March 2011 to present
full and detailed photo restoration log
Did anyone ever figure out if a car dud catch fire?
Yeah, it's dirty. I drive it.
Location: Cecilton (Eastern Shore), Maryland
Posts: 321
My VIN: 802
Club(s): (DMA)
Some information on maintaining fire extinguishers...
Fire extinguishers should be inspected monthly by the owner - make sure it is there, not obstructed and easy to get to, check the pressure gauge or indicator, check for physical damage, check the discharge nozzle for obstructions, and verify the safety seal is intact. Simply put you want to make sure it is there and ready to use.
Fire extinguishers or their agents don't really "expire" (with one exception*). A typical dry chemical (ABC) extinguisher should have an internal inspection preformed 6 years after the date of manufacture and in 6 year intervals after that. 12 years after the date of manufacture (and 12 year intervals after that) the extinguisher should have a hydrostatic pressure test. The 6 year internal inspection can be done the same time as the hydrostatic test. So the service schedule for a fire extinguisher purchased today should be:
2012 - Manufactured
2018 - 6 year internal inspection
2024 - Hydrostatic test
2030 - 6 year internal inspection
2036 - Hydrostatic test
The same service schedule above applies to Halon extinguishers. Carbon Dioxide, wet chemical, and water type will have a different service schedule.
*There is one exception to having a fire extinguisher serviced. A "disposable" type of extinguisher. Typically bought at the hardware store, it will specify on the label that the extinguisher is non-refillable and must be disposed of after any use. These cannot be serviced and are good for 12 years after the date of manufacture. After the 12th year, dispose of the extinguisher and go buy a new one. So if you have any disposable fire extinguishers around your house with a date of 2000 or before, take them out of service and replace.
Personally, I have two fire extinguishers in my DeLorean. My primary is a 3lb Halon BC extinguisher that I have placed directly behind the drivers seat on the parcel shelf. I have not figured out a good way to mount it, but like where it is. My backup is a 2 1/2lb Dry Chem ABC extinguisher I keep in the luggage compartment. I like the Halon because if I need to use it, it will not leave a mess. This model also has a hose, nice if I have a fire in a hard to reach place like behind the dash. It does have it's limitations in that it is not rated for a class A fire (ordinary combustibles) but is rated for flammable liquids and live electrical components. But that's why I have my "backup". I figure I can knock down the fire with the Halon which will give me time to get the Dry Chem out and ready if the fire reignites.
Keep in mind Halon extinguishers of this small size are not rated for typical "Class A" fires such as wood, paper, plastics.